The house honor is complaining that the lights continue to burn very fast like every 2 to 3 weeks he uses CFL (compact fluorescent lamp).1. No fittings on the "conduits".
2. No equipment grounding conductors.
3. If the feeder black is an EGC, it should be on the other bus.
What are your questions about the grounding bus and the bare metal?
saudi arabiaWhere in the world is this?
-Hal
It's 3 phaseI don't know if this is a serious question or not. Is it 3 phase or is the yellow a neutral somehow
Violations so obvious that even young tradesmen would figure out - I thought there was a limit on who posts
Until the 2005 NEC, green was requited for the EGC, but was not restricted to the EGC.If nothing else, I can't think of a place where green is allowed as an ungrounded lead (before 2005? where?).