zemingduan
- Philadelphia,PA
- Electrical Designer
Hi guys. I am now working on the electrical design of a mobile home park design. They have 24 new mobile homes added to the existing electrical system. 8 mobile homes in a row. We need to design the wiring for these new mobile homes. Our proposal is to feed each 8 mobile homes from one 250A breaker on the MDP(The load is calculated per NEC 550). The underground conductors will daisy chain the 8 mobile homes service equipment(see sketch below). The wire length will e around 260 feet. We will consider the voltage drop when sizing the conductors. I didn't see any code issues or violations for this design. All the underground conductors that daisy chain the mobile home can be considered protected by the 250A breaker. What do you think? Do I miss any requirements? What is your typical wiring for a mobile home park electrical system? Thanks!