I looked at a job today. Customer has a 150a service, meter outside, MB panel inside, with what appears to be 2/0 al SE cable.
Customer ordered a 24kw Generac (new model) and a 200a ATS. I will need to replace SE with SER and separate the bonding.
My question is: Since the ATS will have a 200a main, won't I have to use 4/0 SER all the way to the 150a breaker in the panel?