paul Senior Member Location Snohomish, WA Aug 26, 2020 #1 The nameplate says 37A minimum circuit ampacity. Do I use the 75° or can I use the 90° column? Thanks!
The nameplate says 37A minimum circuit ampacity. Do I use the 75° or can I use the 90° column? Thanks!
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Aug 26, 2020 #2 75° C unless you're applying a correction factor. If not #8 THWN is the minimum size required.
paul Senior Member Location Snohomish, WA Aug 26, 2020 #3 infinity said: 75° C unless you're applying a correction factor. If not #8 THWN is the minimum size required. Click to expand... That's what I'm looking for. Thanks!
infinity said: 75° C unless you're applying a correction factor. If not #8 THWN is the minimum size required. Click to expand... That's what I'm looking for. Thanks!