Sizing Jbox with conductors over #4 AWG

Status
Not open for further replies.

crtemp

Senior Member
Location
Wa state
How would I size a box to fit (2) 350, (5) 4/0, and (1) 2/0. Table 314.16(b) only goes to #6. Was hoping to get away with a pvc box, just not sure on the size. The box would have to take a 3” pvc and two 2” pvc conduits as well so I’m sure it would need to be pretty big. I’m just curious on the method to size it.
 
That’s what I am seeing. Thanks for the clarification.
I think that only has to do with a single dimension to the opposite wall. Depth may also be a requirement elsewhere.
Not something I typically deal with.
 
I think that only has to do with a single dimension to the opposite wall. Depth may also be a requirement elsewhere.
Not something I typically deal with.
The only depth requirement is that it be deep enough to accommodate the raceways and their locknuts and bushings.
 
Six for tricks, eight for straight - is a little saying to help remember. Keep in mind that gives you minimum size NEC wants, usually sufficient for pulling through, if you are splicing you may want to increase size beyond those minimum's in some instances. What seems like a lot of room disappears quickly once you start making things up
 
I would think you need to have the proper wire bending space if it's coming out of the back of the J-Box

Sent from my SM-G973U using Tapatalk
 
What about 314.24?
That is not applicable to what Don mentioned. It specifically mentions Outlet and device boxes.

314.24 Depth of Boxes. Outlet and device boxes shall have an approved depth to allow equipment installed within them to be
mounted properly and without likelihood of damage to conductors within the box.
 