I see the raceway as a single turn inductor core, not a transformer with a shorted secondary. Heating in the conduit is the result of hysterisis losses, not current flow.
There could also be some losses from eddy currents circulating in the conduit that are induced by the AC magnetic fields surrounding the conductor. But I think this would be a smaller effect than the loss mechanisms already mentioned.That is a good point, though I think it is fair to say that both aspects are important.
Ferrous conduit will act like a core and you will see hysteresis losses. But if the structure of the conduit is such that it is connected at both ends, then you have a conductive loop acting as a shorted turn.
-Jon
I miss him.The legendary iwire ...
Exception: Conductors installed in nonmetallic raceways run underground
shall be permitted to be arranged as isolated phase, neutral,
and grounded conductor installations. The raceways shall be installed
in close proximity, and the isolated phase, neutral, and grounded
conductors shall comply with the provisions of 300.20(B).
I thought that but apparently can't read.. Thanks, DennisThe conduit must be nonferrous but it must also be in underground
I miss him.![]()
I believe iwire is still here, using a different name.The legendary iwire posted about a 480V service in steel conduit that was installed 'isolated phase', and proceeded to burn up. I've not been able to find this post.
No, he has the same name but has only popped in a couple of times in 2 or 3 years.I believe iwire is still here, using a different name.
Assuming the other end is compliant.This as shown would be OK.
Cutting slots between the holes effectively makes one hole for what we are trying to prevent from happening.Augie47 beat me to it... the BOX that they terminate in must also be non-ferrous....
PS: after the pic was posted:
...or,the penetration would have to be one big hole, not separate penetrations. This as shown would be OK.