romex jockey
- Vermont
- electrician
Hopefully i have this right, but i'm all about you folks correcting me>
210.52C(5) Receptacle Outlet Location. Receptacle outlets shall be
located on or above, but not more than 500 mm (20 in.) above,
the countertop or work surface. Receptacle outlet assemblies
listed for use in countertops or work surfaces shall be permit‐
ted to be installed in countertops or work surfaces. Receptacle
outlets rendered not readily accessible by appliances fastened
in place, appliance garages, sinks, or rangetops as covered in
210.52(C)(1), Exception, or appliances occupying dedicated
space shall not be considered as these required outlets.
soooOOooo, i've yet another 'designer' wanting NOT to see counter top outlets , wanting plugmould under the upper cab's
if the counter is 30", and the uppers start @ 54" , there is 24" in between , bit of a chore when most kitchen appliances only come with that much cord to begin with...
help me out here, is this a bona fide code violation , and should i call this designer out for it?
~RJ~
~RJ~