Is it a "CODE VIOLATION" to run 2 feeders in the same raceway from two different service Disconnecting means, for two different dwelling units...
Thanks for this great response...But you will have to apply the 80% adjustment factor for more than 3 current carrying conductors. That may require an increase in the size conductors.
ThanksNo.
-Hal