Can Romex be exposed across a ceiling in a commercial basement? It is fastened good and follows the building contour.
			What ceiling tiles would be allowable? It is not permitted above a hung ceiling except in one and two-family and multifamily dwellings."Commercial" isn't really a factor. Other than one- and two-family dwellings is really what you mean. It requires it to be protected by a 15-minute thermal finish barrier and only in class III (masonry), IV (heavy timber), or V (protected wood frame). Exposed won't cut it. Cable trays, drywall, or certain ceiling tiles will be allowable.
334.12 Uses Not Permitted.
(A) Types NM, NMC, and NMS. Types NM, NMC, and NMS
cables shall not be permitted as follows:
(1) In any dwelling or structure not specifically permitted in 334.10(1), (2), (3), and (5)
(2) Exposed within a dropped or suspended ceiling cavity in other than one- and two-family and multifamily dwellings
it's just tacky looking out in an open space. just my opinion.
Dropped/suspended is right out. A fixed tile ceiling that mounts to the framing directly would provide sufficient protection (if the tiles are rated as such).(2) Exposed within a dropped or suspended ceiling cavity in other than one- and two-family and multifamily dwellings