366.12 Uses Not Permitted. Auxiliary gutters shall not be
used:
(1) To enclose switches, overcurrent devices, appliances, or
other similar equipment
312.8 Switch and Overcurrent Device Enclosures. The wiring
space within enclosures for switches and overcurrent devices
shall be permitted for other wiring and equipment subject to
limitations for specific equipment as provided in (A) and (B)
(A) Splices, Taps, and Feed-Through Conductors.
***
(B) Power Monitoring Equipment.
assuming wiring all rated
just because it is 24V does not make it a class 2 circuit that has to be separate.Another problem is that the 24V wiring can't be in there. This is the same situation as locating a bell transformer in the panel.
Get one of those RIBs that mounts through a KO with the line voltage wiring. That keeps the line voltage inside the panel and your LV outside.
-Hal
Actually, RIBs come with all conductors routed through the threaded boss.Get one of those RIBs that mounts through a KO with the line voltage wiring. That keeps the line voltage inside the panel and your LV outside.
Actually, RIBs come with all conductors routed through the threaded boss.