CodeQuandary
 - Washington DC
Here's a funny one.
Existing subpanel, single family residence. Run at 240V 30A with older (but apparently fine) 3-wire no ground MC cable. No additional ground lead in the cable.
The ground and neutral are tied together in the panel.
This is a no-no.
In the absence of being able to run a new ground (long difficult run: the client probably won't do it), it would be possible to put the entire subpanel on a GFCI back at the Main.
a. This is actually arguably safer than running a ground and not adding a GFCI to the circuit, I think... (change my mind!)
b. The only way this works is to disconnect the neutral from the box & all the grounds, I believe. Given old house wiring: then (I think) connect all grounds to the box, in case any of them (or the cable) get back to a real ground.
c. An unpredictable downside is nuisance trips, but the house got a whole bunch of GFCI's and AFCIs during some recent work, and doesn't seem to be having any problem with nuisance trips.
Not ideal, but (as inferred above) probably safer than a proper ground but no GFCI. Definitely better than as-is.
Another idea would be to put the (6) circuits each on their own GFCI, but I think that might be less safe than more (the box and cable are no longer protected) and it's definitely more expensive.
Other thoughts?
This is a no-no.