DC Electrician
New User
- Location
 - Arlington, VA
 
- Occupation
 - Electrician
 
I have an engineer indicating that the NEC requires that equipment grounding conductors to loads be installed on "A" terminal bar meaning one only. The grounds are too large for a ground bar and attached with lugs with bolts and nuts to the backbox. The AHJ did not take issue, but this 3rd party insists that the NEC states a terminal bar is required. Can lugs not be used for Panel grounds and only terminal bars even though they are no sized for feed. Also adding a terminal bar with a fork lug is better than putting a lug straight to the backbox. It would seem that is better connection than forked lug that goes into the terminal bar. Any ideas?
	
		
			
		
		
	
				
			
				