I’m hoping to confirm I’m doing my grounding and bonding right for my separately derived system. I have a switched neutral transfer switch that is fed from a service disconnect on the left. The system is 3phase 208v. The gen set has a 225amp breaker. I plan on setting a small piece of 2 1/2 imc on the ground and using 2 1/2 liquidtight flexible metal conduit to get into the genset and the transfer switch... I’m running 4-4/0 copper conductors, and 1 #4awg cu. “3phases, 1 grounded conductor”  and an equipment grounding conductor sized with 250.122. I have a bonding bushing st genset because I’m having to use reducing bushings to get into genset enclosure. There is a bonding jumper installed from the manufacturer in the genset. This bonding jumper is bonding the grounded and grounding conductors, and  should be sized on 250.102(c).  In the transfer switch I’m making a a concentric whole, but running liquidtight flexible metal conduit to get into the ats enclosure. Will I also need a bonding bushing in ats enclosure as well? I have a set of lugs inside the transfer switch that I planned on landing the equipment grounding conductor on.  If I’m understanding 250.30 (a) I also need to run a grounding electrode conductor from frame of my genset to the building steal, this would be sized on 250.66, which should be the largest ungrounded service entrance conductors. These are in the service disconnect and should be paralleled 250kcmill aluminum. Which should be  #2 copper.  as I can’t set ground rods “everything is sitting on concrete, as this install was not planned out very well imo.  It’s going to look like a mess back here because I need to get. 1-2 1/2 raceway, and 3-3/4 raceways 1 for Shilded signal wires, 1-shielded  Ethernet, 2- separate circuits for block heater, and battery charger. This was all designed by previous electricians and in the middle of build they quit or were hired, and fired. I am now working with what I have in front of me. Am I missing any other components of the grounding electrical system ? Does anyone have any better ideas or see a problem with my install? Really want to thank everyone on the forum again! Any and all help is very much appreciated!!!!