Fred B
- Upstate, NY
- Electrician
It does but this where it gets confusing in the 2020 codes.What am I missing here?
Does the code not say that neutrals and grounds must be isolated after the first means of disconnect?
I take it that there is no difference whether it’s an emergency disconnect or a service disconnect.
It was explained to me that it is allowing an "emergency disconnect not service equipment", no ground bonding, to go in ahead of the main service panel where you would still bond your neutral/ground. And you wouldn't pull a ground wire into the EDNSE, neutral bond only.
But if your emergency disconnect equipment is listed and labeled as suitable only as service equipment then you would have to treat the "main" panel as a sub with unbonded neutral/ground.
Your ATS "can" now qualify as either one depending on listing and labeling.