Ambient temperature
WMBELEDES
NY, USA
How should I calculate ambient temperature of a wire if it starts in an oven and ends in an electrical enclosure?
EX:
Conductor runs 10 feet in a 400°f oven and then 40 feet thru a room that is 100°f then 10 feet in an enclosure that is 105°f.
Is it as simple as averages? 150.8°f
Wire is rated for the worst environment 400°f, terminals at that location is rated accordingly. Terminals in the electrical enclosure are rated for 75°c (167°f)
Bill
EX:
Bill
So it looks like you did a weighted average. I think that would be OK if you assume that wire resistance is linear over the temperature range in question.
IMO, you would be okay with the 400 degree ampacity.
(2) Selection of Ampacity. Where more than one ampacity
applies for a given circuit length, the lowest value shall be used.
Exception: Where different ampacities apply to portions of a circuit, the
higher ampacity shall be permitted to be used if the total portion(s) of
the circuit with lower ampacity does not exceed the lesser of 3.0 m
(10 ft) or 10 percent of the total circuit.
Wording for the 2014
used.
Exception: Where two different ampacities apply to adjacent
portions of a circuit, the higher ampacity shall be
permitted to be used beyond the point of transition, a distance
equal to 3.0 m (10 ft) or 10 percent of the circuit
length figured at the higher ampacity, whichever is less.