LLSolutions
- Long Island, NY
Hey Guys,
This is a weird one. Customer is a home heating oil transfer station "Fuel 1993", Big trucks come in to fill the tanks and smaller trucks head out for delivery. They had an underground feeder for two remote pumps and valves go bad. Reusing the pipe isn't an option. They are a few months away from redoing the entire system "project was in final engineering phases when the pumps went out". The facility manager asked if we could temporarily run it overhead and span from the building with the starters out to the pumps in the yard figuring triplex in the air until the new system is up and running. Motor starters are in the basement of the control building and pumps are outside in the yard "outdoor rated pumps". I've done work in hazardous locations before, PVC RMC, EY's the whole 9 but always had engineered drawings spelling out the location classes, but I don't have that here. The existing pipe just enters through the foundation wall into the basement where the starters are and the other end pops up through the grass into a junction box where it then breaks out and hits the pumps and valves in with LMFC "Seal tight". Can i even do this overhead in triplex? Do I need to seal this up at either end?
Thanks
Thanks