jaggedben
- Northern California
- Solar and Energy Storage Installer
I installed a system at my house this past Spring. ~7.5 kWdc / 7.6 kWac SolarEdge system with DC coupled StorEdge inverter. The DC coupled nature of the StorEdge and Solark is a great feature as you only have one grid connected inverter. The Enphase and Tesla systems use dedicated AC coupled batteries if I recall correctly. This makes interconnecting to your house and the grid a bit trickier since both devices can independently dump power to the loads. In our area (National Grid) there is a 10 kW limit on net metered grid tied systems. You could easily surpass this limit with AC coupled solar+storage and the utility could hit you with a price tag of a new transformer at the street.
DC coupled systems also have the inherent benefit of DC clipping recapture, meaning you can safely oversize the PV and have any normally clipped power from the array get dumped into the batteries rather than being curtailed when the inverter reaches nameplate.
Some residential scale energy storage systems are limited to 5 kW of output power meaning you cannot reasonably back up your whole house (an electric dryer is a 5 kW load, for scale). SolarEdge recently rolled out a system called EnergyHub, which essentially is a "smart" transfer switch that gets installed between your utility meter and your main loads center. This 200A rated device allows you to safely island the whole house with a set of StorEdge inverters and up to two batteries (9.8 kWh each) per inverter.
Adding a significant amount of energy storage will raise an eyebrow from a savy local wiring inspector. There are sections in the International Fire Code that will require a 2 hour rated fire room, sprinklered, with a fire alarm and monitoring to a central dispatch. In my research, there seemed to be a threshold at 20 kWh under which these strict and expensive requirements were not not mandated.
Lastly, residential energy storage does not make much financial sense unless 1.) there is an active incentive plan in your area by the utility or the state, and 2.) you lose power once or more per month. The storage equipment for my system was ~$12k.
Interesting comments.
I don't really see more than a marginal benefit to 'clipping recapture.' If your batteries discharged overnight you'll want to start charging them in the morning, before clipping becomes a thing. If your batteries have already charged to full, then the clipped energy still has no where special to go and normal clipping occurs. How often are you actually gonna end up in a window where you're somewhere in between, and how much energy will that amount to? I'm just commenting on my hunch here, but it doesn't seem like it will be that much.