Extend circuit to install lamps and receptacles

Status
Not open for further replies.

Malywr

Senior Member
Location
New Jersey USA
I have question if I Install new lamps and receptacles that mean extend NM conductors. Do I have to protect that section of conductors with AFCI receptacles or entire circuit replace breaker AFCI. Or leaving existing protection as is?
I am not sure if that is in 2017 code 210.12.D which is in my area.


Sent from my iPhone using Tapatalk
 
For replacement receptacles see 406.4(D)
For extending circuits see 210.12(D)
 
For replacement receptacles see 406.4(D)
For extending circuits see 210.12(D)

Ok thank you
New AFCI breaker I think would be too much to trace first outlet and that could be switch too not necessarily receptacle that would be to easy I guess.


Sent from my iPhone using Tapatalk
 