Some of our gas station/convenience store projects have this problem:
Beverage dispenser ICEE machine is on GFCI breaker which is tripping. The dispenser uses a L6-30R receptacle.
The area is moist, but not labeled as kitchen. The sink is more than 9 feet away, but obviously splashing happens from the beverage handling.
We just found out from the manufacturer: "It is recommended for this type of equipment not be connected to a GFCI, the compressor contactor during normal operation will create a spark which the GFCI will interpreted as a short and trip."
I'm thinking as possible solution: remove GFCI breaker and replace with regular 30A-2P breaker. Provide in-use weatherproof cover for the L6-30R receptacle.
Does this sound okay by NEC or what would be the best solution?