All low voltage telecom type circuits are chapter 7.
Read the introduction in NEC carefully. Chapters 1-3 apply generally. Chapter 4 is special equipment and 5 and 6 are special locations. These 3 chapters apply modifications to chapters 1-3.
Unlike those chapter 7 ignores chapter 1-3 unless it specifically calls for it. For instance in the past simply laying coax or CAT5 across a drop ceiling was acceptable (no reference to chapters 1-3). In recent years now it must now be in a raceway, same as general wiring.
It’s not so much a voltage consideration (even up 120 V is allowed in some cases) but it’s a matter of being power limited that sets chapter 7 apart. Generally up to 48 VDC with a few watts is a common telecom voltage. You can run 120 V circuits in the same raceway under limited circumstances for instance.
Satellite LNAs and LNBs today use generally proprietary systems where they inject 12-48 VDC onto the RG-6 to carry power to the LNB. The old K band stuff used an inline power supply but most receivers have it built in and just use a brand specific LNB these days. Some of it originally ran 120 V out to the dish. This is also used for steering motors with K/Ka band or say polar or geosynchronous orbits. The actual RF signals are under 1 V. The low noise amplifier just mildly amplifies and filters the signal to avoid noise from the cabling.