I have a renovation older 60's extra large ranch being done that keeps getting bigger. Homeowner now is moving and eliminating a lot of the existing lighting but all existing wiring is older NM only rated 600C, even receptacles are all split and switched but are only on 14AWG, any code requirements that would dictate the re-wire to the new NM-B? Would like specific code reference to support a change as GC like usual balks at idea, the existing wiring likely may not support requirements for adding AFCI based on issues I've already found. (Whoever did original was not to careful in opening the NM sheathing, slit a lot of the internal conductors and never attempted a repair, so I question condition of the wire terminations boxes that haven't been opened.)

Also neutrals shows browning from heating on some if the lighting terminations. Common issue with older NM.