Eddie702
Licensed Electrician
- Location
- Western Massachusetts
- Occupation
- Electrician
Running some 2/0 SER for a 125 amp feeder (Aluminum obviously). 2/0 has a maximum ampacity of 150A @90C. Why do they use #1 for the equipment ground in the cable? 250.122 says for 150 amp feeder #4 aluminum is all that's required