JoeStillman
- West Chester, PA
- Electrical PE
The local POCO publishes available fault currents for typical transformer secondaries so we can do a SC calc up-front and specify AIC ratings. This is very helpful because the primary infrastructure may not even be designed yet. But what about the Arc-Flash?
Imagine a 600A 480 V service to a new building. My model starts at the transformer secondary and has unprotected cable up to the service main. Using the published max SC current at the transformer of 40 kA and 100' of cable, my SC at the service entrance is 30 kA and I can use 35 kAIC gear.
But my arc-flash will be over 100 calories, which means an unsafe-for-live-work sticker.
In that scenario, I would want to use a main fused switch feeding a MLO panel instead of a main breaker panel so that work in the future can happen inside the panel.
But if I include in my model an assumed infinite utility feeding a 500 kVA transformer with a 1.5%Z and a C12 Bay-O-Net fuse, (never-mind any back-up fuse), I'm at 5.4 calories on the line-side of my main disconnect and my sticker goes from red to orange. What should I do? Assume the worst and include possibly redundant equipment in the design? Or assume the utility will include the protection I imagine on the primary? That's too many "assumes" and no "knows".
Does anybody else make assumptions about the utility primary protection, before the utility company has designed anything?