EGC Sizing error

Status
Not open for further replies.
Location
pakistan
Occupation
student and solar designer
egc sizing


Hello i am having trouble doing EGC sizing


(tag 2 from attached image )
my inverter output current is 120A
continous load = 1.25*120 = 150A
from table 310.15b16
required size is 1/0 AWG ( 170 A)
but for temperature adjustment i take 2/0 AWG and it fullfill my requirement
table 250.122 says that i need 6AWG ,okay cool
but i also increase my egc wire ampacity (NEC apply) so i also need to upgrade EGC wire too

above require wire is 1/0 (AWG , 105600 cir.Mills )

selcted wire is 2/0awg( 133100 cir.mills)
133100/105600 = 1.26

1.26 * 26240 ( 6AWG) == 33073 CIR.MILLS
so my EGC should be 4 AWG

but i am not matching with this image attached calculations for all egc. I do not know where i am wrong

1605545453322.png

1605545502659.png
 

Attachments

  • 1605545387722.png
    1605545387722.png
    68.4 KB · Views: 4
I agree with your calculation.
Since they dont make 5 AWG (33101 kcmil) you would upsize to 4 AWG.
 
If the temperature adjustment requires upsizing then you do not have to upsize the EGC.

You only have to upsize the EGC if you upsize ungrounded conductors for a reason not otherwise required by the code, for example to reduce voltage drop.

Your calculation is correct for a situation where you upsize by choice. But a 6awg EGC is fine in this application.
 
I agree with your calculation.
Since they dont make 5 AWG (33101 kcmil) you would upsize to 4 AWG.
Not sure if you can buy it, but some type G power cables use odd sized equipment grounding conductors including 5 AWG.
 
If the temperature adjustment requires upsizing then you do not have to upsize the EGC.

You only have to upsize the EGC if you upsize ungrounded conductors for a reason not otherwise required by the code, for example to reduce voltage drop.

Your calculation is correct for a situation where you upsize by choice. But a 6awg EGC is fine in this application.
Interesting I never got that out of 250.122(B)
 
If the temperature adjustment requires upsizing then you do not have to upsize the EGC.

You only have to upsize the EGC if you upsize ungrounded conductors for a reason not otherwise required by the code, for example to reduce voltage drop.

Your calculation is correct for a situation where you upsize by choice. But a 6awg EGC is fine in this application.
thanks you are right this pint was missing but now its clear
thanks again
 