The "HP rating" of a disconnect takes into account the possibility of it having to break the LRC of the motor, that's why you need the HP rating as opposed to just the current rating that is equal to the motor FLA. So no.
Although the HP rating is based on a basic 4 pole motor (as the NEC FLC tables are), motors with high pole counts can have significantly higher FLC ratings than 4 pole motors, but the LRC will be roughly the same because it's a function of the kVA/kW and that involves Power Factor, which also changes with pole count in the opposite direction. So bottom line, the HP rating of the disconnect has LRC covered regardless of the motor design.