Mustang125
Member
- Location
- New Hampshire
- Occupation
- Master Electrician, Project Manager and Estimator
Article 110.26 (C)(2) states "For Equipment rated 1200a or larger....." there shall be a door at each end of room.
Now it seems pretty clear but there may be room for interpretation here.
When they say "equipment rated" do they mean the rating of the bus bar or the rating of the wire/breaker that feeds the equipment?
Meaning if I have a piece of equipment with a bus rating of 1200a but I'm only feeding it with 800a, yes the equipment is "rated" at 1200a but there is only a "potential" for 800a.
what are the groups thoughts on this?
Now it seems pretty clear but there may be room for interpretation here.
When they say "equipment rated" do they mean the rating of the bus bar or the rating of the wire/breaker that feeds the equipment?
Meaning if I have a piece of equipment with a bus rating of 1200a but I'm only feeding it with 800a, yes the equipment is "rated" at 1200a but there is only a "potential" for 800a.
what are the groups thoughts on this?