NEC 2011 added which is still in effect NEC 2020
110.26(A)(3) Exception No. 1: In existing dwelling units, service equipment or panelboards that do not exceed 200 amperes shall be permitted in spaces where the height of the working space is less than 2.0 m (61⁄2 ft)
Does NFPA reference the existing dwelling having an existing panel installation that does not require ready access during a remodel or does it reference an existing dwelling having an additional new panel board(s) in a location under 6'6".
If the latter I believe the only limitation to height might be interpreted in the definition of readily accessible
110.26(A)(3) Exception No. 1: In existing dwelling units, service equipment or panelboards that do not exceed 200 amperes shall be permitted in spaces where the height of the working space is less than 2.0 m (61⁄2 ft)
Does NFPA reference the existing dwelling having an existing panel installation that does not require ready access during a remodel or does it reference an existing dwelling having an additional new panel board(s) in a location under 6'6".
If the latter I believe the only limitation to height might be interpreted in the definition of readily accessible