I have been searching and perhaps the wrong phrases in my search. However, the question is this; I am looking to install an 800 Amp 3 phase 480V panel and will be running two conduits with parallel 500MCM THHN-2 copper wires. At each termination there will be Burndy crimped lugs rated 90C. The lugs will be installed with the approved tool. By my calcs the total ampacity of the feeders will be 860 Amps based on table 310.15(B)(16). They will be fed by an 800 amp breaker and the length will not be too long to create an excessive voltage drop.See any problems with any of this?? Thanks in advance.