mhamilton85
- NC
- Electrical Engineer
I am looking for recommendations on how best to route a new circuit into an outside breaker panel. Photos below. What the original builder did in 1996 (for whatever reason) was put a large outdoor panel just for the high load circuits, and then a 100A sub panel inside the house for lighting and outlet loads. I'm looking to add a 50A circuit for a NEMA 6-50 receptacle in the garage using a 6/2 NM cable. Here is the issue:
The original conduit feeding the crawlspace is full, I can't add the new 6/2 through that opening. My plan was to punch out the other rear conduit knockout on the left lower side of the panel, using a 1" or 1.5" diameter, but from my measurements it will be running into a floor joist.
There are plenty of knockouts in the bottom of the panel, but I'd be below the sill plate and to make that option work either have to drill through the brick (least favorite option), or make a 270 degree turn and then back into the crawlspace through the rim joist. As you can see the area around the panel is cluttered with telco, cable, and the service entrance.
Do I just drill my own hole through the backplate toward the bottom center? Or overdrill the LH internal knockout slightly to the right? Or is there a better option altogether?
Thanks for any advice,
-Michael
-Michael