winnie
- Springfield, MA, USA
- Electric motor research
You don't get it, I don't get it. You are asking us to explain the thought process of someone I disagree with.
Jon
Jon
Jon
A drawing from the equipment mfg should be supplied, so the AHJ can see whats being provided, if its separate cabinets, panels etc, needs to be shown and interconnection details
It appears pretty simple to me, but I've encounter this situation many times. Customer acquires a machine built for a voltage other that what they have. They want to use a transformer they have , or buy a used one for cheap, and connect it in reverse. I've seen many do it. They don't realize that the output coil is nearly always a delta coil, and there is no simple way to ground it, other than corner ground it, or leave it ungrounded. Neither do they realize what the implications are of leaving it ungrounded and floating or corner grounding it. From a safety aspect or equipment operational problems or damage that may result from doing so.
A lot of equipment today built as standard, doesn't play nice with an ungrounded or corner grounded supply. Most new equipment with any electronic requires a grounded wye supply to be reliable. Codes and listings aside, if I'm going to do it and accept the liability and support for the equipment, I want it done right. No mater what the buyer, salesman, line assembler, engineer or inspector thinks. I understand the difference and make it proper or I walk.
It seems clear in this case that the vendor selling the equipment, supplied the wrong transformer, and doesn't understand the difference. The machine builder clearly built the thing for a 480V grounded wye, and the machine dealer cobbled on the wrong type transformer to make the sale. And the customers contractor doesn't understand either.
The codes and standards are not a how to manual or a design manual and should not be used as a substitute for knowledge about the system engineering and design. Nor should they be used as a workaround, to get past inspectors, engineers or designers that aren't fully up to speed with the situation at hand.
This job needs the correct transformer, bonded and grounded properly, and that can't happen with what the vendor supplied. Simple.
I don't think you are fully understanding the discussion. The issue is not that the machine is delta or Y but rather whether the power source supplying the machine is delta or Y. The vast majority of equipment today expects to be supplied from a grounded Y system. In some cases it is critical but in almost all cases it is desired for a number of reasons.Will ask the engineer to provide datasheet for coil machine see if it’s 480V delta or 480V wye. If it turns out 480V wye then your right but 480 delta then it’s different story. Won’t be long time till I can do this.
I think MTW summed it up well.
huh? If the engineer gives me machine manufacturer data sheet that says machine accepts 480V delta then what’s the problem? It’s per manufacturer instruction 110.3(B). Otherwise if the manufacturer datasheet indicates 480V grounded wye then it’s clear need to change. I am mostly code enforcer Not designer so I can’t tell them to change otherwise if it’s like design decision. Note engineer can again come back with what he had originally its premise wiring as well. Why the engineer provide that’s all.....[/b] unless specifically permitted by the manufacturer[/b]. But as noted many loads will work fine with delta sources .
-Jon
Better would be to ask if the equipment can function reliably on a corner grounded 480V delta system, as that's the only way your transformer output can be grounded. I would ask for it in writing.
If I get manufacturer datasheet of the machine and control cabinet indicating delta is ok or Not ok would that not be same as manufacturer permitting?
In addition Would it also be better to ask to manufacturer leaving it ungrounded equipment function reliably also?
With a delta, your possibilities are:
1) corner grounded
2) high leg grounded if your transformer has a center tap on one of the secondary coils
3) ungrounded
The drawings you posted suggested an ungrounded supply, but did not have ground fault detection.
It is worth asking the manufacturer if the ungrounded connection is acceptable, because that is what the supplier drawings show. However IMHO the ungrounded setup is a bad idea for numerous reasons.
-Jon