Don't think so.Just guessing: something related to 'Circuit Total Limiting' breakers that restrict 'skinny' breakers to a subset of panel locations.
-Jon
Would make sense if it were attached to a tandem breaker. Every one I seen like OP pictured is on a two pole breaker just like he has.It's a device to keep you from putting a tandem in certain slots. This stems from the days where there was a limit on 42 poles in the panel.
So apparently sort of like having a type S fuseholder so you can't easily put in too large of a fuse.
Over 60 (maybe 70) amps and those breakers back then spanned across both sides the panel and took up four single pole spaces. That alone provided a fair amount of securing/stability of the unit. Then if it were a main breaker it still had an additional hold down clamp.The QO circuit limiting feature is a 'hook' not this tab.
I only saw this tab on larger ampacity breakers. I have never seen the official description of why they existed.
My technical literature from 1960 does not mention this construction. My guess is they were to provide stability when the larger conductors were used with 2 pole breakers in the older metal interiors. A similar construction existed on 2 pole QF fusible devices.
Over 60 (maybe 70) amps and those breakers back then spanned across both sides the panel and took up four single pole spaces.
Doesn't make sense to have them today, but back then maybe it did if it were like I said a similar thing to having type S fuseholders.
According to my 1960 spec sheet, there were no 'factory' supplied spaces for the 30A and larger breakers. The hole would be punched in the field by a not 'unqualified person'.Just guessing...
Perhaps a rejection feature that would only allow the higher amperage breakers to be installed near the top of the panel?
My daughter’s house has a 1960 vintage QO panel that I’ll try to go have a look at once I’m out of quarantine!
According to my catalog, there were no 'factory' supplied spaces for the 30A and larger breakers. The hole would be punched in the field by a not 'unqualified person'