mwm1752
 - Aspen, Colo
There are no other conduits/tubing that contain the statement " any combination of ambient and conductor temperatures is in excess  " I can find in my search. I have a few thoughts on what this means but I'd appreciate specific input for final analysis. Here are my thoughts toward what "combination refers to"
(1) The LFNC will have markings that refer to ambient temperature rating of the conduit.
(2) All conductors are subject to adjustment per NEC article 310.
(3) The size of the conductor will determine the conduit size.
(4) Ambient temperature is determined by yearly average?, Highest possible at any moment? or Highest possibel for a continuous time period? to start the conductor adjustment.(please endorse just one for specifics)
So in a nut shell the combination refers to the conduit temperature rating is appropriate with the surrounding conditions and the sizing of conduit due to conductor circular mils.
ARTICLE 356 Liquidtight Flexible Nonmetallic Conduit: Type LFNC
356.12 Uses Not Permitted
LFNC shall not be used as follows:
(2) Where any combination of ambient and conductor temperatures is in excess of that for which the LFNC is approved