Ground rods
Your chart shows resistance reduce to 30% with 4 rods while 2 rods resistance was 60% about half. How more than 2 does not accomplish much?
The law of demishing (sp) returns, 2 rods is reduced by 60%, 3 is 40%.
Its not worth any time on why, just drive 2 and go home.
I have a paper from Mike Holt and 1984 IEEE on why 25 ohms but its too large to attach. But basically he said 25 ohms is calculated based on 7 miles of 8 AWG, on the premise of earth wires, or using the earth as a ground return, as related to telegraph systems
Following picture explains the theory of adding ground rods in parallel. More than 2 does not accomplish much. This picture is from AEMC, they had an excellent publication on why ground rods are copper coated, size of ground rods, depth of ground rods.
So its drive two and go home.
Thanks for initiating the explanation to address my concern about the inconsistency of this rule. Now it is making a lot more sense.
Please connect the dots.
No metal pipes in the kitchens and baths?
No grounded metal anywhere?
Extraordinary claims call for extraordinary proof but this may not be an extraordinary claim. I can't say at this point.
His point being, that if all the metal you mention is bonded properly, connection to dirt has no meaning or effect.
That and the now normal use of an ufer.
Another point illustrated in the diagram is the spacing of the rods.
A ground rod discharging to the ground affects the earth in its immediate vicinity. Placing the second rod too close does not allow the rods to be used to their best advantage. Six feet is code, but ten feet gives better reduction of ohms on an 8 foot rod.
New construction is using concrete encased/UFER/ rebar etc....
BTW what does UFER mean or stand for. I read from EC&M its the name of the engineering ( Herbert G. Ufer ) who created it as a solution. Ill buy that unless someone tells me otherwise.
Ufer is the last name of an engineer who "discovered" or designed the first concrete encased electrode. I think he was an army corp engineer who was trying to solve static issues in desert conditions, specifically for munition storage? I forget the whole story, it's probably on wiki
Some engineers say twice the length of a rod. 10' rod calls for 20' spacing.. I imagine at some point we hit diminishing returns
All has to do with "sphere of influence" which will vary depending on soil conditions.
I think studies have shown you need at least 6 feet separation in most any soil conditions or what you gain is pretty minimal.