220.14(J) Dwelling Units
Motors rated less than 1/8 HP and connected to a lighting circuit shall be considered part of the minimum lighting load.
220.84(C)(4) - Multifamily Dwelling Calculated Loads
The nameplate ampere or kVA rating of all permanently connected motors not included in items (3)
Regarding above new rule 210.14(J) in NEC 2020, does this mean if we apply this rule, only motors equal or greater than 1/8HP have to comply with 220.84(C)(4)?
Motors rated less than 1/8 HP and connected to a lighting circuit shall be considered part of the minimum lighting load.
220.84(C)(4) - Multifamily Dwelling Calculated Loads
The nameplate ampere or kVA rating of all permanently connected motors not included in items (3)
Regarding above new rule 210.14(J) in NEC 2020, does this mean if we apply this rule, only motors equal or greater than 1/8HP have to comply with 220.84(C)(4)?