hhsting
- Glen bunie, md, us
- Junior plan reviewer
Does anyone know of transformer primary is 480V three phase delta to secondary of 240/120V single phase?
Why would you need such a transformer? Wouldn't a 1Ø, 480 volt primary work?
Should be common as dirt in moderate sizes. How big do you need? (Google turns up a lot of hits- give that a try)
You have a 1Ø primary and a 1Ø secondary, there is no 3Ø wye or delta involved.Do 480V to 240/120V transformer have delta or wye windings primary and secondary which?
Look at 250.20(B)(1).I am just thinking about grounding such transformer. If one does not know the winding then how does one ground or not NEC 2014 Section 250.30?
Delta and wye don't apply to single-phase transformers- see the diagram at https://www.se.com/us/en/product/EE50S3H/xfmr-dry-1ph-50kva-240x480v-120-240v/#mounting-1
Secondary only. The 480 volt feeding the primary is already grounded somewhere else.So only the 240/120V side need to be grounded Not the primary 480V?
You're creating a neutral by grounding the secondary.Ok but secondary conductor I see 2 phases 240/120V does not have neutral? I dont follow which terminal would have neutral?
I dont follow. On the wiring schematic below link which transformer terminal would be the neutral X2, X3?