FaradayFF
- California
Greetings, All -
Recently, I've witnessed an installation where the existing MV(11kV) circuit consisted of unshielded cable. The cable was installed and commissioned years ago. What's more, it's been in continuous operation for 50+ years.
In my recent training, I was taught that the medium voltage cable needs to be shielded so that the electric field within the cable is confined, the cable is protected from induced voltage, and other reasons. However, here I come across the installation that seems to be operating fine without the shield. It appears the MV cable construction utilizing the shield has come on scene only recently?
Does anyone can recommend a good source of literature that talks about this topic? I'd like to learn more in depth about this.
I've also just recently seen an installation where a star point of a generator is grounded to Neutral Grounding Transformer utilizing a cable with insulation rated for 1kV. The generator is rated for 11kV. If the machine has experienced a ground fault, how can the cable sustain the voltage level that is greater than what its insulation is rated for??
Thanks,
EE
Thanks,
EE