electrofelon
Senior Member
- Location
 - Cherry Valley NY, Seattle, WA
 
- Occupation
 - Electrician
 
I googled that erikson number and they dont say whose breaker they use, but they do say "MDL breaker" and googing that looks like an eaton M frame MDL3800.  In the Eaton catalog that is showing as the std lug being a 3/0-400 3 conductor lug.  Erikson for some reason apparently isnt supplying that, but the part number for that lug is TA800MA2, should be able to swap it out (assuming I have inferred the correct breaker).
Edit: for those who are curious, in the Eaton catalog, the (2) 500kcmil lug is showing for a 700A max breaker.
	
		
			
		
		
	
				
			Edit: for those who are curious, in the Eaton catalog, the (2) 500kcmil lug is showing for a 700A max breaker.
			
				Last edited: 
			
		
	
								
								
									
	
		
			
		
		
	
	
	
		
			
		
		
	
								
							
							
				