You do not even need the 83% rule if the calculated load on each panel is 180 amps or less per the next size up rule.Size of conductors/ampacity. Can 4/0 aluminum be used in a residential application for a 400 amp service feeding two 200 amp panels?
I'm getting at the 83% rule/diversity of the loads/ and if they carry the entire load of the dwelling.
Here it is accepted routinely even though a load calculation on each panel could be requested.
(actually 2/0 Cu is also)
Smart stateOur state kept 310.15(B)(7)...![]()
I would think and interpretate on 2/0 copper, if not supplying entire load(which will not be with 2 panels) , you must size over current protection device to its next standard size breaker which is 175A.Here it is accepted routinely even though a load calculation on each panel could be requested.
Ok, let's say calculated load is 351 amps. 175 amps will be installed into one panel, and 176 amps will be installed in the other.I would think and interpretate on 2/0 copper, if not supplying entire load(which will not be with 2 panels) , you must size over current protection device to its next standard size breaker which is 175A.
Load calculation could also be requested on 4/0 Al too, but as Infinity stated would have to be no more than 180A.
Thoughts?
Compliant because the next size up rule would allow the 180 amp conductor to be protected at 200 amps.Ok, let's say calculated load is 351 amps. 175 amps will be installed into one panel, and 176 amps will be installed in the other.
Electrician installs (2) 200 panels with 4/0 aluminum SE to each. Compliant, or no?
Possibly for the one of the panel, but not the other.Compliant because the next size up rule would allow the 180 amp conductor to be protected at 200 amps.
You lost me, one panel is 175 amp load with a 180 amp conductor the other is 176 amp load with a 180 amp conductor so what's the issue?Poss
Well then that changes my answer in post #11. You would have to move 1 amp of load to the other panel to use the #4/0 aluminum.The issue is bad math...lol, sorry. I meant to put 181 amps
Today I did a "400 amp" single phase service to a 5 gang meter pack for 4 dwelling units plus house panel. Two sets of 4/0 AL in same pipe. Technically it's a 288 amp service.