Ok those were the original readings. I had them come out because it was over 5% and also for them to further diagnose what was wrong. They wound up re-taping the transformer to get the voltages within 5%. These are the values after they retapped
Secondary
Tap changed
Went From D to C
VFD % 89.6
VAB 487
VBC 475
VCA 488
IA - 433
IB - 385
IC - 272
For all of the people thinking that this could be an issue with the “ VFD “, again we have 3 other newer smaller vfds running and working, able to run and they also have this this unbalanced amperage but our large drive is not able to handle it.
This is a Utility Issue!!!!
What is the correct terminology that I need to use to go to the Utility with, in order for them to further investigate and repair this problem with their feed for the Pump station ? They have come back and claimed they are within ANSI standards. The standards are for 3% nominal voltage. Are there no standards for amperage ? I need to reply back to the Utility with further info regarding this situation and that’s why I came here in the engineering section to get some advice.
Secondary
Tap changed
Went From D to C
VFD % 89.6
VAB 487
VBC 475
VCA 488
IA - 433
IB - 385
IC - 272