NewtonLaw
- Honesdale, PA USA
If someone would provide a picture of the transformer installation it would help as would the operating voltage.
If you want to calculate the fault duty yourself all you need to do is come up with the impedance at the point of fault. You can do this by placing a capacitor across the service entrance with no load attached. Measure the open circuit voltage before adding the capacitor, then measure the voltage again after adding the capacitor. The short circuit kVA is approximately found then by:
kVAsc approximately = kVAR / ((V-with cap)-(V-without cap))/V-without cap
This will give you the approximate symmetrical short circuit duty that includes the service conductor, transformers and supply system to the point of fault. (the point where you connected the capacitor).
Also, you did not say if the service is three phase or single phase and at what secondary voltage?
From Eaton, they supply a 45 kVA up to 75 kVA three phase pad-mounted transformer at 208 volts with impedances that range from 2.7% to 5.75% This would give you a range from 3,621 amps to 7,710 amps at the terminals of the transformer assuming an infinite primary bus.
Hope this helps.
Hope this helps.