In order to transform the 150m outdoor cables to 4000a busduct, don't we need OCPD cable protection at the busduct fitting (End box)?
 
You need to protect the conductor at its rating. If the ampacity of the cables and the busway are at least what the upstream OCPD is set for, then not OCPD needed at the transition.
 
You need to protect the conductor at its rating. If the ampacity of the cables and the busway are at least what the upstream OCPD is set for, then not OCPD needed at the transition.
I think the ampacity of conductors must be equaled or larger than OCPD (No exception), isn't?
 
No OCPD is required at a transition between cables and busway, assuming that the ampacity of both are equal to or greater than the supply OCPD rating.
 