I think the ampacity of conductors must be equaled or larger than OCPD (No exception), isn't?You need to protect the conductor at its rating. If the ampacity of the cables and the busway are at least what the upstream OCPD is set for, then not OCPD needed at the transition.
4000a busductWhat is the rating of the OCPD for the circuit? What is the rated ampacity of the cables?
I meant for >800aI think the ampacity of conductors must be equaled or larger than OCPD (No exception), isn't?
Does it has something to do with rating?No OCPD is required at a transition between cables and busway, assuming that the ampacity of both are equal to or greater than the supply OCPD rating.
Both the cables and the busway are conductors...as long as they are protected at or below their rated ampacity, there is no need for any additional protection.Does it has something to do with rating?
ThanksBoth the cables and the busway are conductors...as long as they are protected at or below their rated ampacity, there is no need for any additional protection.