I would caution you however about the thinking that switchgear is just like any other control system and that generic off the shelf PLCs and control equipment is perfectly acceptable to the task. From experience it’s not. There are a lot of issues to be concerned with in switchgear. Caterpillar has built a lot of switchgear over the years using Schneider or Eaton breakers and GE or AB PLCs. Cat uses their reputation and buying power with the genset side of things to sell this stuff to larger municipalities, prisons, and federal facilities. Durham, Raleigh, and several state facilities in North Carolina have them so I have quite a bit of experience with them. In terms of reliability there are a lot fewer problems with ASCO ATSs, or switchgear using multifunction relays. These solutions are both purpose built for the application. You just don’t have “the usual” PLC problems, even if they buy an embedded/OEM style PLC and repackage it as a generic looking breaker control.
DCS control is popular with larger power plants. Or more specifically they typically have a layer of multifunction relays that handle faults and the DCS is little more than an outrageously overpriced HMI. The multifunction relays came about from the evolution from induction disc to today’s microprocessor units.
Don’t get me wrong here. You can certainly write your own PLC program to do everything inherent in say an SEL 751. But then you need to do type testing...throwing thousands of automated function tests generated by software at it to test every possible outcome plus analysis of the results. There is specialized relay testing gear specifically for this. But you won’t save any money doing it and it’s so much easier to just accept an off the shelf solution.
This is like burner controls. Most large burners have two levels of controls. The lowest level is almost invariably either a Honeywell or Fireye branded burner safety relay. It handles the actual burner lighting process and actively monitors everything at all times. The PLC sits on top of this and controls the overall process, adjusting heat output, and making pretty operator displays.
So just saying...go with the road well traveled here.