JMCDONALD70
- Tennessee
- Electrical inspector
I have just recently attained my ICC certification for electrical inspector and hope to be starting new job soon. I have been doing lots of research in the 2017 NEC and the IRC. My question relates to mobile home service conductor sizing. After the meter if one uses a Mobile Home disconnect with the usual 4 circuits, and let's say they come out of there to get the well pump and the outside condenser. Now let's say this is a 200 amp service. From the disconnect into the mobile home wouldn't you be required to use 3/0 copper which would make your incoming service conductors 3/0 since no feeder conductor can be larger than incoming service conductor. It seems to me you can't use the 83 percent here because the disconnect with the circuits. Everyone around here uses 2/0 in this example. Thanks