PE (always learning)
- Saint Louis
- Professional Engineer
I've got a project where a 25 KW solar array is being provided on the load side of a panel rated for 600 amps. The incoming service is 120/208, 3 phase, 4 wire and I want to verify that my main panel bus rating is adequate for the 25 KW solar array. I don't deal with solar that often and I just want to make sure my assumptions are correct. For this issue, I would defer to 705.12. The solar array has a FLA of 69 amps and I have located the breakers for the main and the PV source on opposite ends of the bus bar. If I calculate according to 705.12 (B), I would take (1.25*69 amps) + 600 = 686.25 amps. This is less than 1.2*600 = 720 amps. Everything checks out and the 600 amp bus should be adequate. Please let me know if I have misinterpreted anything.
Best Regards
Best Regards