RossS
- Research Triangle, NC USA
- Electrical engineer
I have a job that requires a 750KVA 208:480/277V step-up. The contractor submittal is for the same transformer configured as a step-down. When I returned the submittal to "revise and resubmit," the contractor said they'd just wire it in reverse. I denied that strategy as it isn't my design. The contractor is pushing back hard (causing me to suspect they already released the order).
As an Engineer of Record, would you accept this, understanding the near certain litigation and potential liability if the contractor improperly reconfigured the grounding for the derived service moving from the low voltage side to the high voltage side, or improperly sized the over current protection? Are there other significant factors I may be overlooking?
Thanks all.
Thanks all.