Here is my situation In more detail so you guys can advise me with the better method to go
I have couple of server racks and customer wants me to bring a ground conductor to the room. At first, I assumed the server racks should be already grounded with the branch circuit but customer admits the server racks are not grounded.
However, my first thought is to Install telecom ground busbar next to the server rack. Then, Pull a ground conductor from the nearest panel and connect it to the ground busbar. Now, that Tom explains about the high impedance it causes when ground wire is separately installed I’m worried.
The second thought is if the branch circuit is in EMT, instead of pulling ground conductor from the panel that is further away, I can tap from the EMT and use #6 AWG to ground bus bar
Now, let’s say if the nearest panel is 40 ft away from the server rack, what size of ground conductor would you guys use? Per Ron slide 23, 2kcmil per ft, that makes it 1AWG ground conductor