Can OCPD/Fuses be mounted in a combiner box on the roof under PV Modules? This is for a micro inverters install with enphase inverters. The question is about the fuses being readily accessible.
Thanks, I agree that the Fuses/OCPD for the strings need to be readily accessible, 690.9D does not exempt them as they are not PV Source/Output circuits. They are inverter output circuits and must be readily accessible.
The aggregator does have fuses.
This installation is simply inline fuses in a roof mounted Soladeck box. These are not readily accessible and would be a violation in my opinion.
Hmm, so I don't really know the reasoning behind the word-smithing in 240.24 in the last two cycles, but it seems to me you'd have to be back on the 2014 NEC to call it a violation. Also there is exception 4 which arguably applies here.
What your describing is not an uncommon practice, and without seeing a clearer safety danger or a less ambiguous code section I would not consider this a violation.