mbrooke
Batteries Included
- United States
- Technician
The purpose is so that if you have a small service, like a monument lighting, etc, which may only need a 20 amp service because minimal load, you cannot have a 20 amp feeder coming from the meter to your main 20 amp disconnect.
I would imagine a 55 amp limit there is because lots of old services used to be 60 amps in a tiny round can. Could possibly have a max load in a house of 30 or 40 amps. Gonna have to have at least 60 amp feeder to main
The feeder goes from the service entrance to anywhere there's a connection to branch circuits.Wouldn't the feeder be after the main disconnect?
Apologize... I don't think that link I posted has anything to do with the question and my edit time has expired.
So why must it equal the service size?
I just confused myself. Lets say you have 4/0 AL (180-amp) 200 amp service. It goes to a disconnect. From that disconnect to the main panel can it be 180 amp wire or does it need to be 200 amp rated wire? Thought 200 amp but just confused myself with 4/0 SER. Man I made a mess of this post. Calling it a day.
Bogus rule if ask me. Nothing wrong with having smaller conductors if you've got an OCPD.
I think you're thinking breakers, but I think the issue was small sized fuses in a main.Bogus rule if ask me. Nothing wrong with having smaller conductors if you've got an OCPD.
If you had a 60 amp service to a meter, then put in 30 amp fuses in the main pullout of a 4-circuit panel, and fed it with #10 from the meter, it could easily have fuses changed to 60 amp
But if you had a 200 amp service to the meter, and had a 100 amp panel, I think those fuses could not be easily changed to larger ones.
I think
For what it's worth, this thread brings back a memory from a while back. I did a service call at a very small older house that had been rehabbed as a rental. I had to get into the panel, and I saw that it was 100-amp - but it was being fed from the meter with 10 gauge wire.That could be what the code is getting at now that I think about it.
The feeder carries the load for the service is the statement - simple main disconnect to structure panel that has all the branch circuits of the structure. If your MDP has a buss for branch circuits & you have 1 circuit being fed from that buss along with a feeder then the minimum limit is NA. I'm betting the 55 Amp # is tied to 230.79(D).I think you're thinking breakers, but I think the issue was small sized fuses in a main.
I think