We install breaking resistors with Allen Bradley VFDs. The installation instructions for the resistor instructs you to place a contactor in front of the VFD that will open if a temperature switch in the resistor opens up. They cite a risk of fire.
Would ignoring this requirement be considered a code violation? I'm thinking it violates 110.4(B), right?
I'm thinking:
I'm thinking:
- "Listed and labeled equipment" applies to the VFD. It doesn't matter whether we're listing our control panel under UL 508A - the VFD is always listed.
- Does "any instructions included in the listing" include the installation instructions? Or do I have to find the listing and see if the installation instructions are specifically referenced?