Bonding Around SharkBite Copper Plumbing Fittings
infinity
New Jersey
Journeyman Electrician (retired)
Has anyone ever seen a bonding jumper around these push to connect fittings? If a copper water system used these fittings and the fittings provide isolation for each section of pipe is it no longer a complete copper piping system? Sounds like it would be many isolated sections of pipe and not a system. According to the manufacturer these fittings do not provide adequate bonding of the sections of pipe they're attached to.
SHARKBITE GROUNDING ON COPPER PIPE
When connecting a SharkBite Universal fitting to a copper piping system, install a copper jumper cable to ensure proper grounding. SharkBite Universal fittings are not an electrically continuous fitting.
Anything on the "load" side of such a fitting would be bonded, if necessary, by the EGC of the equipment likely to energize it.
With the amount of frozen pipe repairs lately I wonder how many plumbers used these?
One question is if you were required to bond the interior copper water piping system because the water main is plastic {250.104(A)}, would a system comprised of copper pipe and these non-conductive fittings require bonding?
I've never seen a plumbing system made up with SharkBites, only repairs and small additions.
If there is a continuously-metallic main section of the plumbing system, that's the section to bond.
If the entire system was made with non-conductive joints, I don't see how it could be required.
I agree it's more hypothetical than practical. If there were only one fitting in the system IMO that fitting would require a bonding jumper.
(Sorry, I rearranged and added to my post)
It could be argued that it depends on where in the system it is.
If near the middle, I would agree; if just feeding one or two fixtures, then not necessary.
I agree. The fittings are too high to use throughout an installation.
Around here they are used for pex mainly.
For copper I would use compression personally